As an aside I need to do a calibration myself, although I know cell15 is the outlier so I just tend to nudge* that cell towards 3.65V where the BMS (3015) will decide that's the battery full. That with a few forced discharge cycles keep it reasonably sane.
Having said that its common in summer to be >1kWh out on SoC and I think that's probably the cause of all the overvoltage warnings. Same as last year etc. If the battery is 10% out on SoC then the inverter may not reduce charge current (10 step stuff, begins at 90%) at all before the battery BMS hits OV alarm.
*automation changes charge rate if SoC is out & basically blips the battery until cell15 hits 3.55V, which will then top out at 3.61V & the SoC is "right" - well 100%, which may not be the case etc etc.