Tim Concerning your comments about eco mode, I agree that I would like to leave the AC3 to sort it out and if it behaves as you say then there is nothing to do. I have two problems. Firstly I don't like leaving the batteries at 0% SoC and you have said it shouldn't happen, and that is fine - I can ask GE. Secondly, I have an EPS CU in the house which I fitted 10 years ago but have never used as such, and it supplies important items (all small loads), and I have arranged for it to run from the EPS output, and so I want to set a battery reserve which might not be much, but say 10%. I have not connected the EPS CU to the inverter output yet - I am waiting to ensure that the inverter behaves as I want. So I understand that I should ask GE for a software upgrade to allow for this.
So, if the grid fails, can I assume that the battery reserve which was previously not available to run the load will become available to support a load via the EPS output?
Your point that setting the discharge power to zero blocks discharge but allows charge from solar suits me because there is so little spare solar I could leave it for weeks without the battery being full to capacity. This would obviously be a temporary manual setting. I will try this to see what the inverter does.
You say that timed discharge can be used to prevent use of the battery to run the house load as well as to permit it. That is an interesting addition. And so, if I enable timed discharge and use 00:00-00:00 do I effectively block the inverter from using the battery to supply the load? And similarly if I enable timed export and use 00:00-00:00 do I block the inverter from exporting power to the grid? I understand that in both cases the use of eco mode would continue to enable the transfer of spare solar power to the batteries.
I have noticed that if I have time charge (and it may apply to the other timed modes) set for 00:00-23:59, ie all of the time, and I set a charge level then the batteries will charge to that level. However, if I then change the charge level without changing the time then the inverter ignores the change. This could be that the code is looking at the time and not at the level, and if a time threshold does not pass then it does not consider that there might be a level change. Is this possible? I have rebooted the inverter in order to reset awareness of the level but it still does not seem to see the change. Only when I later reset a number of other items (battery options) did it suddenly notice the change.
Thanks for your help. Your discussion entry could certainly form the basis of a Wiki page describing the operation of the AC3 inverter.