Just had the grid EM115 replaced with a 'GEM120CTM'. It is IEC62053-21 Class 1.0 classified. I assume that GEM stands for Givenergy Energy Meter. It looks like the default screen/display is the current power in Watts. They didn't change the CT clamp. With both inverters paused and solar switched off I assumed that it should agree with the Home Display (SMET2). There is also a G100 meter - it agrees with the Home Display. However with the oven on the HD shows 2.06kW, the G100 meter the same - but the GEM says 590W.
This Grid meter is important to the Givenergy system - is the GEM a heap of junk, wrong CT clamp or am I looking at the wrong thing.
100Amp CT clamps are typically accurate to plus or minus 1% from 10 to 90 Amps. Below 10 they are less accurate. The installer is saying that there is nothing wrong - is he talking out of his Foul Gas Exhaust sphincter?
Goodbye to the EM115
Slartibartfast didn't replace the CT with a different meter make/model and now the power measurement is out by a factor of 4. Hmm...
stevelewis ct’s are ct’s - just different ratios. So it may be the meter wasn’t setup to suit the ratio. Though I would have thought most domestic meters are 100A.
Or is it the secondary ratio is now 1A not 5A? Though you would expect a different error.
Actually looking at the meter reference it could be a 120a meter. So that could make my theory possible.
OK - Givenergy responded to my question. The two CT clamp are different - hence both the meter and CT clamp have to be changed.
I was a bit shocked by the reply. I sent the question - e-mail- at 11:51. The reply came through at 11:59. It used to take them weeks or months to reply - are things changing?
Slartibartfast Maybe the response is quick when the answer's easy?

From an image of the GEM120CTM the label shows '230 V 0.25-5(45) A 50 Hz 3K6', and it is described as a 45 A direct connected, 100 A CT connected meter.
The EM115 shows '1-20(100) A', so it is not surprising that the CT ratio used is different between the 2 meters.
It looks like the gem120 meter is an eastron sdm 120 meter with the sd letters changed to ge. Had a system installed a couple of weeks ago with one of these but unfortunately it's not been possible to get the meter working. Paid to have a givenergy engineer come to look but rather disappointing they are not able to provide a date when they can visit.
Thanks. Yes definitely worth considering trialling the different meter.