I thought it might be useful for those Folk with multi battery / controller set-ups, to have a separate place to discuss issues & ideas - in the hope that this would prove valuable to new owners just starting out - as well as those planning or considering new systems.
I've recently had an installation of 2 X 8.2 batteries - each with it's own AC 3.0 Coupled.
The reason for 2 controllers is that I wanted to have plenty of available ESS, but also be able to run the 'Golden hour' as I call it, for the evening cooking session, with (as close as poss to) zero grid import. Bearing in mind that just switching on a kettle in the UK will practically gobble up the max output from one AC Coupled, I decided to go with one 8.2, each with it's own controller.
Altogether, I'm pretty pleased with the performance.
Here are some numbers from last Saturday for the half-hourly usage in Whrs (not kWhrs!) around the evening Golden hour. Numbers in the final column are the HH grid import from the SMETS2 meter (via Octopus), whilst HWSBO simultaneously used the kettle/oven/ hobs etc:
Sat-06-Nov 18:30 19:00 4
Sat-06-Nov 18:00 18:30 4
Sat-06-Nov 17:30 18:00 2
Sat-06-Nov 17:00 17:30 5
Sat-06-Nov 16:30 17:00 4
Sat-06-Nov 16:00 16:30 2
Sat-06-Nov 15:30 16:00 3
I'm pretty happy with that.
Downsides...
GE have said that the current firmware doesn't work particularly well in the 'Multi-plant' environment, but hope that new firmware, not due out until sometime next year, will be more robust.
Issues I've experienced so far have been:
- One controller/battery discharging into the other
- Un-demanded charge & discharge at max chat
- Asymmetric charging / discharging
These seem to have been 'teething' problems, which appear to have been resolved by the deployment of a script onto the controllers, which monitors them, and re-starts them if they go AWOL.
Seemingly, one or both of the controllers loses comms with the EM115 meter, which sends them into a tail-spin.
There's one particularly annoying issue which still prevails though; in marginal weather, when the PV output is relatively low (2 - 3 kW ish) and erratic cloud cover means the PV output is pulsing up & down, one or both controllers are in a state of almost continuous flux, building up a charge, then 'tripping' out (presumably re-starting at the behest of the script) which affects both controllers, such that all of the surplus energy bleeds off to the grid. This seems to cycle over a period of about 5 mins or so.
Not entirely sure, but it seems worse when there's a split between the two battery SoCs (or should that be SsoC? !).
I've tried various mode changes, and splitting the modes, but to no avail.
Eventually, they sort themselves out - particularly if the PV surplus increases - but it's annoying to have spent so much spondula, only to see surplus energy weeing out into the grid for the DNO to sell onto an energy company, who in turn will flog it to my neighbours - at peak-price, no doubt!
Anyone else had similar issues?
To anyone considering a similar system, please don't let this put you off; all-in-all I really like the GE products, I'm very pleased with my purchases, and given the same situation, I'd choose exactly the same system again.
Despite it taking too long to get through to the support guys sometimes, when you do talk with them, they listen carefully to any issues, swiftly log-in to your system, and can talk with a good level of understanding about your issue, or query.
Clearly, a huge amount of work has gone (is going) into the new portal, and GE are constantly improving the end-user experience. Keep it up Folks!
Great to have a forum at last, too!