Can anybody advise on what the PV data highlighted below in the photo might mean? It looks a bit suspicious to me?
Many thanks
Suspicious PV data


Cdent
I have two strings, both south facing with no shade until late afternoon so both strings should be producing very similar readings. This just happens in the morning's on sunny days as it ramps up to about 1 kW. Throughout the rest of the day and when it isn't bright sunshine, both strings produce similar readings.
So, if we presume that there is a problem with the string, only when it is sunny and steadily increasing in Pv production in the morning, what on earth could be the fault? Bit of a tricky one๐ค

Cloud9 wonder if it's a similar issue as found here: https://community.givenergy.cloud/d/2042-generation-sudden-drop-when-weather-consistent
Do you have either microinverters or DC optimizers for each panel?
Note the drop in current on string 1. Check your connections and (if you know how and can do it safely) the output of each panel. Something is pulling the string down.
cluelesscris
But only pulling the string down as the sun is coming up higher fairly early in the day and PV levels are rising fairly quickly. When it's not sunny and PV levels are relatively low and fluctuating everything works just fine. System hasn't been installed long so still under warranty so difficult to persuade installers there's a problem! I'm trying to get as much info as possible please so I can tackle them again. Thanks
Out of interest, how many panels on each string?
I am going to assume you have the panels wired in Series as that's standard in the UK and all PV panels are the same.
In that case you would add the Voltages of the panels together and the Current (AMPS) would be the same as the rating on the rear.
Using the above image as an example - 10 panels in total, 5 per string - you would see each strings producing 5 x 41.2V = 206V and Current would be 11.7A (all of these are maximum values).
For Watts (Power) = 206 (volts) x 11.7 (amps) = 2410 Watts (2.41kw)
If you have a bad panel then the entire string will be affected by the lowest common number. Example if 1 panel was only producing 5 Amps then the calculation would look like;
206 x 5 = 1030 Watts (1.03kw)
So the ENTIRE string is affected by a reduction in output.
If the problem is intermittent then that would suggest a connection issue rather than a panel issue as a panel issue would be constant and a connection issue may get better (or worse) with temperature or water.
Hope that helps