If it has always done this, I would also do the following test: Turn off the first system completely and check that the other system works as expected, with sensible numbers on the graph. Then turn off the second system and do the same for the first system. That will rule out any installation issues on one of the two systems (e.g. one CT clamp round the wrong way).
If that is all good, then I suspect it may be some kind of interaction/fight/oscillation between the two - possibly because the 2nd Gen hybrids have a faster response time, creating a positive feedback loop, perhaps???
But I also agree with Hoggy, that the timings of the rows in your data looks wrong - so do as he suggests as well.
Do you see two entries in the Inverters section of the Portal. If yes, do they both have different 'Inverter SN' and 'Dongle SN' values?