New smart meter…

7 comments started 2023-04-23 last 2023-04-23
Mobile App
O
#1 ONEIL

I’m getting a replacement smart meter installed soon…the old first generation one didn’t provide an export figure so I was unable to get the benefit of an SEG arrangement…obviously the power supply will be disconnect during the switch… is there anything I should be concerned about or do to ensure my system returns to normal function ( connectivity etc)

Thanks in advance…

Mick

H
#2 Heald642

ONEIL Hey bud, recently had the exact same thing. Told the installer we had solar panels and a battery to make them aware and they had no issues with it. Had no issues with everything turning back on etc and didn't have to switch anything off.
Hope this helps

O
#3 ONEIL

Hopefully it’s the same for me…I asked the installers yesterday but as yet they haven’t replied…it’s the weekend so perhaps they will tomorrow…thanks for your reply…I’ll post if it all goes well…(or not..!! )

C
#4 cluelesscris

ONEIL Most of the time it won't be a problem but occassionally you may need to shut everything down a restart it after they have gone as it may not recover when the juice is back on. Essentially, the meter change should just look like a power cut and therefore should be tollerated by your installation. When I had my smart meter upgraded the inverter failed to reconnect to the battery so a graceful shut down and restart was needed and everything was OK. Do tell the installer what you have. As a precaution they should isolate your system before starting work just in case it doesn't auto isolate itself when the grid goes down and give him a nice jolt when he or she is least expecting it.

T
#5 TX200

Also, if the CT clamp is on the tails coming out of the meter (rather than being the other end near the consumer unit)..

Check what cable it’s on before the smart meter appointment. Check which direction the arrow is pointing in.

So if the smart meter person puts it back on the wrong wire or the wrong direction, you’ll know what’s wrong when all the data looks wrong!

Also check it’s properly clipped on, not loose.

C
#6 cluelesscris

TX200 Seriously good piece of advice....

#7 Hook

When I had my smart meters replaced, I told the installer. No problem he said.

He removed the busbars from the EMS switch and put the CT Clamp on upside down.

Had to get my installer out to replace the missing busbars. 😫