I have 3 x 8.2kw batteries and recently had the much discussed issue of batteries displaying significantly different charge levels (SOC) in aggregate and individually.
Knowledgeable & helpful Givenergy engineer visit today as pre-arranged. He was sent based on the log data as they thought there might be a faulty cell in one battery. Partly based on the voltage data that he said gave more reliable information than SOC. Sounded feasible?
However when stripping down offending battery discovered several connections were not tight by 2 or 3 full turns. Obviously not good! Cleaned up and remade connections. Checked other batteries (which were fine). Started a calibration.
I will monitor in coming days. His view was that the firmware update may not make a difference in this particular instance but will of course apply it once released.
I guess others with similar issue may consider its worth reviewing data for voltage as well as SOC in case there is anything to glean. I would've thought the loose connection issue is rare but perhaps not a one off? In my case I'm not sure what the voltage differences were or what range is considered "normal"?
If I understand correctly the normal voltage should be 51.2VDC - from the Features information in datasheet.
But will I be right to think it will be higher at peak charge and less at full discharge? As mentioned I don't know what range should be considered normal? I will be grateful for guidance so I can monitor in a meaningful way.