After a few emails back and forth to GE (thanks for their patience), it looks like I’ll have to live with the EPS limitations:
I have a plant setup (2xAC3 and 2x 8.2kwh batteries). I have an EPS setup for one of my AC3.
I had hoped that the EMS would allow both to be set up to continue to work in a power cut. Confirmed however that whilst the EMS would probably still be powered, it wouldn’t provide any benefit due to a lack of sine wave from the grid allowing for the inverters to remain in sync.
No way to connect both batteries to one inverter in this case so I have access to both via the one (despite this being how many systems are configured, I.e one inc, multiple batteries).
So in a power cut situation, I lose 3kw of discharge (ok I can live with it if needed as we are generally a fairly low base load except when cooking etc), and 50% of the installed battery capacity. Only way around it is to a) have split consumer units (one for each, not clear if this would still cause a sine wave issue) or b) stump up for AIO replacement.
Neither of which is palatable. What I don’t get through is AIO (or Tesla PW) both can be stacked behind their gateway and both are AC coupled. So if you have more than one - how do they avoid the sine wave issue?