I'm seeing repeated backup overload faults and before spending a lot of money with an electrician I'd like to be sure I'm understanding correctly.
I have a method 2 EPS setup on a 5kw inverter with a new EPS breaker box which the installer populated by moving existing circuits from the main box. I asked (probably wrongly) for ground and 1st floor sockets when I actually needed fridge (from gnd) and 1st floor sockets where router etc lives.
My assumption based on the timings of the faults - lunch or dinner time(ish) is that the kitchen is triggering this - I guess what confuses me a little is that the kettle alone is c. 3kw/h and that runs a lot through the day with seemingly no issue.
Q1. Even though there is no power cut the 2.6kw/h limit is there for any circuits fed by the EPS box? I've seen other posts saying that's so but the wording in EPS docs is confusing as that says circuits will be fed by solar/inverter until a cut. 99% certain it's how it is but would like to be 100.
My EPS breaker box has 2 breakers labelled a). GND/1st Sockets and b). Kitchen Grid. Sockets makes sense but when I switched of the kitchen grid one nothing happened.... Installer did not document that but I will get it reverse engineered as I wouldn't trust any answer from them.
Q2. In addition to the two breakers there is a meter labelled CT and I'm confused as the EPS docs from GE do not show any options with that. Unclear to me if that's used for something else. Any thoughts?
My intention is to get an electrician in and most likely change to a fully manual switchover EPS to remove the issue. When originally installing I assumed failover was instant but I now see it's about 5 secs anyway so the router will die anyway. Only disadvantage I see is that if I'm out of the house then the fridge won't be protected. Will discuss with the electrician and ask for options.