Tim if you are happy to unscrew it and give the connector a push to see if it clicks in, it'll rule something else out.
Thanks Tim and everyone else
Here is the story so far:
The inverter is not receiving data about the house/mains
The CT clamp is a little loose but presumably has always been like this?
The EM115 is showing changing values - does this mean it is receiving data from clamp?
I have removed the cover below the inverter and reseated a pair of connectors where the data cable terminates. I then restarted the inverted for good measure.
Result:
At first appeared no change - House Load still being registered as zero.
But could see a load had been briefly registered during my tinkering.
Pressed data cable firmly again up into inverter and load registered!
THANKS Tim!
Not sure why they were loose - no tension on wire.
Need to keep an eye on situation (as I write “No Load” showing again)
Wasn’t looking forward to 4pm Flux import time today.
Thanks all