Have a look at my post https://community.givenergy.cloud/d/3111-combine-eco-mode-and-timed-export/17.
The text on the portal "... discharge batteries to your home..." for "timed discharge" is indeed very confusing. I've been emailing to and from with GE and what the timed discharge setting actually does is "... force discharge to the grid UNLESS there's a demand from the home and then priority goes to home and only after that to grid.
GE explained that they are modifying the export and discharge settings (some changes are already visible under the "remote control" section of "my inverter").
Just like yourself I've gone through testing out all possible permutations and I found the one that works. Bottom line is do not use "timed export" as that automatically disables ECO and you will therefore import from grid rather than draw from battery (yes - that's correct).
You can however combine ECO + timed charge + timed discharge. If you don't want ECO, you can leave that off as well.
You'll see that if you change timings in timed discharge, it will adopt the same in timed export (even though you have disabled that).
I'm now on:
- ECO : enabled
- timed charge: enabled from 4:45-5:00am upto a max of 9% (that works for me in case I drop to say 6% and I need some extra cheap juice before the sun comes up)
- timed discharge: enabled from 16:47-19:00pm (in my case that usually exports my battery from 100% to about 12% - leaving me just enough to get through the evening and night on the battery).

Hope that helps and confirms you are not alone with interpreting GE's mystic language. Soon a new set of settings will come out apparently which will be more user-friendly and easier to understand. Finger's crossed.