Been getting the above notification over the last two weeks, about once every couple of days. Does anyone know what it means and if I need to be doing something? The notification clears after 5 mins.
BMS Under Voltage
Is it somewhere cold?
Update. I’ve just matched the notification times against the System Settings and it seems to occur when the battery drops to 0%. When the notification clears 5 mins later, it pushes the battery to 5% using grid energy. Now before the update in June (I think?), the battery would never go below 5%. Since the update it occasionally does.
What is the battery voltage when you get the notification?

4.25am Battery voltage is 45.32, batter watts 50. You see the battery goes to 0% at the end


Steve0898 so 4001 is the eon 'special' firmware that basically runs the 5.2 battery at 100% DOD.
There is a whole thing on this because e.on essentially sold them based on a misprinted (but surprisingly long lived) datasheet from GE which said the 5.2 packs were 100% usable (they are normally 80% so about 4kWh)
To get around having their a%% handed to them legally, they got their own firmware which really does push these to their extremes (like running a calibration each time) which results in it hitting the lower and upper voltage alarms.
Expect a reduced lifespan and more alarms as the packs get older/more cycles.

It’s all weird behaviour since the update. I’ve set the discharge buffer to 5% to try and support the battery life but it still goes down to 1%