Going to grid

5 comments started 2023-12-31 last 2023-12-31
GivEnergy Products
J
#1 Jayesh

Hi all,
I’m not sure how should I stop my electricity going back to grid. As I charge batteries on night due flux Tariff. But it seems always going back (not much) but is there any way I can stop it.
Thank you

S
#2 SteveCook

Hi
Are you on ECO, that will stop it.
How much is not much? In kWhr over 24 hr period.
50w for 10 seconds is half of b****r all and is probably the inverter just responding slowly

V
#3 Vestas

SteveCook The inverter responds a lot faster than 10 seconds but the apps/portal doesn't.

I suspect the OP is another who doesn't realise he's not seeing live data in any way, he's just seeing a snapshot every 10secs/5mins (depending on whether he's using the app locally or not).

FWIW the "leakage" to grid due to loads/PV inputs changing on a Gen1 hybrid is under 16kWh in 6 months here. ie bugger all as you said - and if there's an export MPAN in place then you get some pennies anyway.

The way to tell the difference is simple - read the smart meter export total and subtract the "meter" export total found under "My Inverter" on the portal. That's the "leakage" the inverter/EM115 meter doesn't see. Note that even if you don't have an export MPAN you can still read the smart meter manually to check the total.

K
#4 KevinB

My AIO was recently firmware updated to 0.609 (from 0.605) and BMS 8 (from 7) and anecdotally the "leakage" is a lot lower. I don't know if that's better reporting, faster inverter response, or just an illusion, but I think it's better (and that's what counts, right?).