Just had a notification pop up yesterday on my inverter saying BMS Overvoltage, doesn't explain what it is or the significance of it, only lasted 5 minutes before it cleared.
What does this mean and is it something that pops up from time to time? Never had it pop up before.
G
#2Guzz
I've been getting this BMS overvoltage notification recently too, often accompanied by a red light on the battery status indicator. I've emailed Givenergy support, but have had no response as yet.
T
#3Turnipfarmer84
Guzz OK cool. If you get a reply let me know. I only had it the once thankfully
#4TheDragon (GivEnergy)
It means the voltage reported by BMS of your battery is above the allowed threshold, charging will cease to protect the battery. Its around 58v if I remember right. A fully charged battery will peak at 55.5-56V. Look at your charging voltages, over a 24 hr period, you will see it slowly rise as the battery charges. Then it will begin to rise more suddenly around 54.5v, this is the im full point.
W
#5wilfleek
The upper and lower battery voltage alarm figures were changed in a battery firmware update last year:
"BMS(3002) 15/10/2021
1: the overall low voltage alarm is changed from 41.6V to 45V, and the overall high voltage alarm is changed from 58.4V to 57.5V
2: The battery balancing function is enabled "
G
#6Guzz
This is the response
"Nothing to worry about they are working OK. I believe this is just an issue and notifications popping up relating to the % indifference sometimes caused with dual batteries as a display error."
N
#7NorrisP
I had this for the first time today, It was cleared at the next stats period. It appears to be associated with the battery reaching 100% (Single 8.2kWh battery) As the stats period is 5 minutes, we get no indication of when within the preiod this conditon occured and for how long it remained active. I think it would be good to have an explanation for such notifications within the portal giving the conditions which cause the notification to be raised and cleared. In addition maybe a severity category for notifications.
L
#8lightningad
Is this the same as “ backup overload fault”? Just had a single notification of the inverter page of the report, again lasted for a single 5min block.