Seems sensible enough - its obvious the fire brigade have had a large input.
Basically don't install batteries anywhere inside the house which is an escape route (so no installs under stairs, in corridors or near exit doors/windows), don't install in the loft or integral garage unless it has a firewall/fire door which will contain a fire (structurally) for 60 minutes and don't install anywhere that people may sleep. Integral garages should have that level of fire protection anyway if they were built in the last 35 years, lofts won't unless they've been converted and they're precluded then because its an area people could sleep.
Outside regs are likely to prove a good bit more problematic. You can't install the battery within 1m of doors, windows, vents or escape routes.
Also of note - you can't install more than 40kWh of storage indoors unless the area its installed in has firewalls/doors and will contain the fire for 60 minutes. If it is you can install a maximum of 80kWh of storage.
Edit - also batteries installed outside on a driveway or inside a garage will require additional mechanical protection which seems sensible in case they get hit by a car.
A (linked) smoke detector is required for most installs which aren't outside.
The rules on ventilation don't apply to Lithium Ion batteries, they're more for lead-acid where hydrogen can be released.
Pretty sure that 80%+ of current installs would fail the new standard, however as with all building regs, they are not retrospective. They will however apply to the system in its entirety if you install any further equipment (or replace existing equipment) so that's one to remember.
Edit2 - also makes sense of some things installers said/asked regarding double boarded ceiling and fire alarm in garage. They were obviously aware of this last July - or their parent company (the housebuilder) was.