Hi,
I wonder if anyone else is seeing this?
When I have set the battery to charge to a particular level, and it has reached that level, any solar power is used to charge the battery and the load is supplied by importing. I don't want it to do this. I want to prioritise solar supplying to the load first, if the battery level is above the reserve level, and to import to charge the battery if it is below the Charge To level. I thought that's what these settings are intended for?
Product: GIV-HY5.0
Version: D0.913-A0.913
Summary: When 'Timed Charge' is enabled and the current time is within the 'Start Time' to ''End Time window, but the battery level is higher than 'Charge To', solar energy only goes into the battery and not to the load. Import is used for the load. It should prioritise load and then battery, as it does when not within the time window.
Steps to reproduce:
- On dashboard, go to My Inverter: Settings: Timed Charge
- Set Enabled on, Start Time to an hour ago, End Time to an hour hence
- Set Charge To to slightly less than the current battery level (assuming more than 4%)
What happens: Solar power goes to charge the battery. Import power is used to supply Load.
What should happen: Solar power supplies load, any excess goes to charge battery.
Why? Because the battery charge level already exceeds the "Charge To" setting.