Hi all,
My solar panels seem to spend more time exporting to the grid, rather than charging the battery.
Anyone else have this scenario?
Thanks,
Mitch.
Feeding grid more than storage battery.

Yes we only have a 5.2kWh battery and it is generally charged mid morning at this time of year, so we export more to the grid. For example today we have exported about 22kWh.
MitchP My system does this, but only because I explicitly configure it to.
Once the battery approaches full, the charging rate can slow down. But if it's only half-full, that might be a problem.
The inverter does have an upper limit on charging rate - 2.6kW for older inverters, 3.6kW for gen-3, and probably higher for AIO. So if solar is a lot higher than that, the inverter will max the battery charging rate and has to send the rest to the grid.
As I sit here now, the battery is at 10%, the panels are generating 2.5kw and most of it is going to the grid.
Might be worth checking your battery charging rate.
Hi, I think I was just seeing some sort of routine export, apparently it does this to keep the connection with the grid active :