Timp You are not likely to see any clipping as the potential generation from your panels is well within the restrictions of your inverter. For a Gen 3 3.6 inverter you'd have to generate more than 3.6kW to see clipping, but it can probably handle up to 7kW of generation if you are charging the battery at the same time.
I have a Gen 1 3.6 inverter, the limitations are a bit more severe with a max generation of 2.8kW per string and 4.8kW total.
Generally if you have clipping the graph of PV production will show clipping as a flattish line at the top of the generation curve rather than a smother curve, for example:

This a plot from last summer (as we don't seem to have summer this year) string 1 can produce 3.2kW, but never does as the inverter can only take 2.8kW from it. String 2 can generate at least the same but is throttled so as not to exceed the 4.8kW. The line is uneven as the inverter manages the inputs but there is clipping between 11 and 3.
You'll see at 15:10 a sudden drop in string 2 output, this is because my battery was fully charged so the inverter could only use 3.68kW.
Here is one without clipping: