Folks
I thought it might help those of you with a zappi and an ESS (Energy Storage System / home battery) to know about a setting hidden deep in the zappi, to help control your ESS battery (batteries) whilst EV charging in ECO+ mode.
Problem - the zappi can't maintain its min 1.4 kW for ECO + operation, because the ESS keeps nicking the surplus PV / Wind generation!
2nd problem - when charging in ECO+, the zappi nicks energy from the ESS, which I want to retain, for later use!
The tendency is to change the ESS settings, such that it won't discharge during the times you're in ECO+ mode, but this varies with the weather, and you'll probably need to keep changing your programmed times.
Solution - the zappi has a couple of setting deep-down in the bowels, which prevents the above issues.
It's called 'Avoid' ...
Options are:
Avoid Drain
Avoid charge
Avoid both
The zappi needs to be fed with CT (Current Transformer) info from the ESS, but a good installer should give you this feature, anyway.
The settings are within the advanced menu, so you'll need your passcode (or the default one), and can be found in:
Other settings / Advanced / Supply grid / Network / Battery
Here are a couple of excerpts from the manual, on the subject; (unfortunately, I don't seem to be able to insert images into posts, other than as links):
Installation
zappi operation and installation manual
Battery Storage Systems (page 41) for more information about battery storage systems.
The table below details the different settings for working with an AC coupled battery storage system:
Setting, Function, Description
'None' There is no battery system installed.
'Avoid Drain' Stops the zappi (or other linked myenergi devices) draining the battery when using surplus
power from the solar or wind generation.
'Avoid Charge' Effectively allows the zappi (or other linked myenergi devices) to take priority over the battery
when charging from solar or wind generation.
'Avoid Both' Provides both of the above functions. This setting will normally provide the best compatibility
'Limit to Gen' Will limit the output of the zappi (except when boosting), to prevent unwanted draining of an AC
coupled battery system. This setting does not require a CT to monitor the battery but does need
a CT to monitor the solar/wind generation.
Note: This setting is to support legacy installations â it is preferable to install a CT to monitor the
battery and use one of the settings below.
Battery Storage Systems
AC Coupled
Where there is an AC coupled battery storage system, there can be a conflict as both the storage system and the
zappi are competing to consume the surplus energy. Whilst this is not necessarily an issue, the results can be
somewhat unpredictable.
There is the option to add an additional CT sensor to monitor the battery storage. This will give control as to which
device has priority. The additional CT sensor should be wired to one of the CT terminals in the zappi or harvi device
(if wireless measurement is required). This CT should be clipped around the live cable of the battery inverter with the
arrow on the CT pointing away from the battery and towards the consumer unit/fuse board.
During the setup process it will be necessary to change the setting for the appropriate CT to AC Battery; refer to CT
Config (page 24). Also refer to Supply Grid â Network Settings â Battery (page 23) for information on setting the
'priority' of battery systems.
Hope this helps some Folk - give me a 'like' it it's helped you. Thanks.