Battery discharge rate halved

3 comments started 2024-11-04 last 2024-11-05
GivEnergy ProductsHybridBattery
W
#1 Will_J

Whilst running the battery down this evening the discharge rate fell suddenly from 3.6kW to 1.7kW and it's been stuck there since - see this graph:

This hasn't happened before, I know that charge rates are limited when it's cold but I didn't think the same applied to discharge. Does anyone have any ideas?

#2 hoggy

If its not a stuck power level setting and this is on discharge only (so low temp does not apply) then I'd hazard a guess you have a cell going low voltage in your battery which the BMS will see and reduce rate.
I'd suggest using a 3rd party app like: https://play.google.com/store/apps/details?id=uk.rubikcube.invertermonitor&hl=en_GB and click on the battery bar at the bottom to monitor the 16x cell voltages.

Is it a 9.5 pack by any chance? Seem to be common issues with cell 5, 9, 13 on those.
Any that differ massively is what your looking for.

W
#3 Will_J

So it charged overnight and it seems like it's working ok again this morning...

Yes, it is a 9.5. I downloaded that app (thanks for the rec) and this is the current state-of-play:

They all seem pretty close, apart from Cell #1 - but I don't know what the normal range of values should be and whether this is outside what it should be.