SimonClarke To a limited extent I have the same issue but it isn’t the wind particularly but the outside temperature. It is cooler indoors when it is warmer outside.
I have two LG Therma V heat pumps. The weather compensation (they call it ‘AI’) mode is pretty simple and its all based on outside air temperature (OAT) at the heat pumps and leaving water temperature (LWT) from the heat pumps.
Mine is set:
- LWT 30 with OAT 14
- LWT 52 with OAT -2
Between the two OAT’s it adjusts the LWT proportionately.
So if your house is too cool with a warmer OAT, you either increase the upper OAT (so stretching the curve over a longer temperature range) or increase the LWT at that upper OAT (so the radiator water is hotter).
Bear in mind that these are maximums and minimums of LWT that the heat pump will go to, so if its less than -2 degrees the LWT won’t be any higher than 52, and if its warmer then 14 degrees the LWT won’t be any lower than 30 degrees.
My installers didn’t set any heat curve they just set it to a fixed 55 degrees I think so presumably they didn’t have to come back with me complaining the house was cold. Electricity consumption clearly not their problem.
I’ve got to my settings through trial and error tweaking the LWT’s up and down if the house was too cold in deep winter or too hot in milder spring. I’m sure I could do it more scientifically but I just checked and I haven’t changed it since April last year so it must be about right.
The other thing of note is to make sure that the room thermostat is set high enough so that it rarely turns heat pump off during the heating period. On mine the thermostat acts as a master for the whole system so if it turns off then there’s no heating until the temperature falls in that room (the hallway in my case).