My portal shows no PV data from 10:30 07Dec24 following an outage caused by Storm Darragh.
All other data - grid, load, battery - seems to be displaying OK.
I reported this to GE on 17Dec24 but have had no response - hence post to this forum.
I have a Giv-AC3.0 AC coupled inverter with a 9.5kWh battery.
The outage was for a few hours and when the power returned it was low voltage for a while before returning to normal voltage.
I have done all the obvious checks:
- isolators/RCBOs/MCBs etc all on/OK
- PV system is operating OK: inverter switches on/off daily; inverter indicates power when generating; main PV generation meter operating OK
- EM115 meter in DB is displaying OK, and tallies with the PV inverter display; generation current displayed also tallies with a clamp meter measurement on the PV circuit
- have reset/reconnected WiFi connection to the inverter dongle - dongle shows continuous light
- have done a hard reset (turned off inverter & battery for 10 secs)
This appears to be a problem with the inverter communicating with the EM115 PV generation meter.
Any ideas/advice?