Is inactivity a problem for batteries?

8 comments started 2025-01-17 last 2025-01-17
GivEnergy ProductsBattery
G
#1 GribinIsaf

I am sure this has been answered in the past - I have done a search - sorry.

We are briefly (a few weeks) between TOU tariffs so no cheap night time battery charging.

At this time of year there will not be any surplus generation going into the batteries. Without intervention they will just be looked after by the inverter at minimum SOC.

Is this ok or should I be giving them some grid charge?

Thanks

AC Couple Giv-AC3.0
2 x 5.2Wh
1 x 5.12Wh Gen 3

S
#2 SteveCook

could try running winter battery conditioning

G
#3 GribinIsaf

SteveCook could try running winter battery conditioning

Thanks for tip

G
#4 GribinIsaf

SteveCook could try running winter battery conditioning

Just looked at it: "Winter Battery Conditioning mode will cause your Inverter to charge / discharge batteries for 10 minutes when their temperature reaches 2°C" Batteries inside house should not reach 2 degrees!

G
#5 geoffreycoan

If your batteries are idle and empty it shouldn’t cause a problem because if the battery SoC does drop below 4% then they will automatically charge themselves up a bit to prevent damage.

Having said that, in general its better to exercise the batteries than to keep them empty for long periods of time, so maybe do a force charge for a bit every 4 or 5 days. No real need to fill them up entirely, just charge a bit and let them discharge. If you are getting reasonable solar generation then that’d be happening anyway

G
#6 GribinIsaf

geoffreycoan Having said that, in general its better to exercise the batteries than to keep them empty for long periods of time, so maybe do a force charge for a bit every 4 or 5 days. No real need to fill them up entirely, just charge a bit and let them discharge. If you are getting reasonable solar generation then that’d be happening anyway

Thanks. Your last sentence does not apply today but we can hope!

W
#7 wrighar

If the batteries are not to be used (charge or discharge for a period of time, I'd charge them up to about 40% and turn ECO off.
When stored before sale, around 40% is the sort of charge level used, and is good for months.

G
#8 GribinIsaf

wrighar If the batteries are not to be used (charge or discharge for a period of time, I'd charge them up to about 40% and turn ECO off.

Thanks for that