Inverter.

6 comments started 2025-02-05 last 2025-02-05
GivEnergy ProductsAC Coupled
B
#1 Barnboy73

inverter stopped working yesterday after various micro power outages. no lights on. Dongle no light . Lora transmission unit no light. Tried to reset. No success. Power not tripped. MCB ok. Any ideas

D
#2 DD

Barnboy73 If it's a hybrid inverter, did you also disconnect the battery when you tried to reset it? I think I've seen suggested that you disconnect all power sources (grid, battery, PV), perhaps wait a few minutes, and then power back up.

There should also be a meter in the mini consumer unit - EM115 or something like that. Is that working (displaying numbers)? If not, seems unlikely that it would fail at the same time, which would make me double-check all MCBs and RCDs all the way back to the incoming supply.

B
#3 Barnboy73

EM115 operational.|Emlite meter operational. Next move?

D
#4 DD

Barnboy73 Did you try the full power cycle ?

I'm not sure if it's a useful test to power on only the battery. Actually, not sure if you mentioned whether the battery had any lights on.

B
#5 Barnboy73

Battery lights on, on both batteries. Not very electrically minded. Explain full power cycle?

D
#6 DD

Barnboy73 As I said above, disconnect all power sources from the inverter : grid, battery and PV.