I have been getting loads of these errors (as the sun has been shining quite a lot). I thought it may have been my system that was at fault. I am measuring the grid voltage and when my PV system was turned off the voltage went down below the requirement 253v. However:-
An update on my voltage issue:- (very interesting)
Raised a complaint to SSEN on Sunday, they phoned me up at midday to inform me about a visit by an engineer later today (max 3 hrs)
Engineer turned up at 3 ish (very knowledgable and willing to chat through what’s happening). Asked about my system and then said this is all on us and nothing you’re doing is wrong.
He pulled the fuse and measured the voltage so no import or export) and it was 252.8v (so .2 short of the max allowed)
He said he was in the office when the complaints team sent the request to his department, so was able to do some homework before he left (for visits)
Logged onto my smart meter and can see the readings now and back dated. Could see the over voltage. Looked at a few meters in the local area as well and saw all were going over during the day (in this nice weather) as well.
Next he looked at the local sub-station and said it was 11,580v. All substations should be 11,000v. He then looked at a few sub-stations and saw all were above 11,000v.
This meant it was an Area sub-station not a local sub-station issue. He phoned the person that looked after that and they agreed it was an issue. He would turn down the area sub-station voltage (today or first thing in the morning).
My guy would then log back onto the local sub-substations to see if they were back to 11,000v. If not adjust them up/down to get to the correct voltage.
He then said once this is done the sub-stations are automatic and will keep the correct settings going forward. E.g as my local sub-station was 11,580v this is what it was automatically changing to meet this requirement, once at 11,000v it would keep this as the new target.
Lastly he said he would keep my job card open, if I still see an issue to ring up, he will check things again and get them adjusted if needed.
So loads of points to SSEN my local DNO (thank you guys)