I posted this on the Facebook group but had no replies so thought I would try on here.
I have another "issue" with my 2 battery setup - which Martin has previously suggested a calibration - which sort of worked in that they did both come back online and work together.
But the other day, the 8.2kWh Gen1 decided to just sit there and not charge or discharge. So I waited until the evening and set a calibration off, which it started at the prescribed time and started to dump to grid.
Next morning, it was still in calibration mode and the master 9.5kWh Gen 3 battery had discharged, but the 8.2kWh battery was just the same.
Rebooted the inverter and the BMS voltage dropped to something like 8v - so I turned off the 8.2 and rebooted and all was well and the system worked fine all day (But reduced capacity)
I think the basic issue is a mismatch of battery voltages, so as calibration isn't sorting the 8.2 out, I thought I would force discharge the 9.5 and see if they can get close enough to be happy to re-join.
No such luck and the 8.2kWh is sitting at about 11% SOC and 3.2V per cell (51.268 total)
The 9.5kWh has recharged overnight and is sitting at 3.31V per cell and 53.051 overall.
Main overall BMS voltage is 51.31V
Anyone got any ideas what I can do to sort out my system? Its not particularly urgent at this time of year, but would be nice to be able to sort it out and whilst I will contact Giv Support officially if i can't sort it out, they probably have more urgent issues to deal with at the moment!
Update from this morning. The primary battery was discharged fully last night, with the two battery voltages at one point At leat, being aligned but it didn’t reconnect the second battery and it’s still hanging.