Dashboard says Batteries are 100%

3 comments started 2025-08-12 last 2025-08-15
GivEnergy ProductsBattery
B
#1 BrianSolar

I have qty2 5.2Kwh batteries in my system. Overall the dashboard says the batteries are at 100% so the charging is idle and the system is exporting to the grid. However, if i look at the Primary and Secondary battery individually they are at 98% and 96% respectively. Is this normal?

K
#2 killythebid

BrianSolar
Yep pretty much. What the inverter thinks is the SOC and the individual batteries BMS thinks are two different things. You could try a calibration which initially may "fix" it but it will soon drift again to somewhere near what you are seeing now.

I have X2 5.2kWh too and although my batteries are not showing the same stats as yours the difference between the Primary and Secondary can be about 10% SOC.

B
#3 BrianSolar

killythebid Many thanks for the reply