AnonymousHooman Before the relay change our CU RCD's used to trip on changeover. This was mostly fixed a couple of years ago, soon after install, when the whole N-PE relay issue blew up for GE AIO. I believe since then GE ensured the relay was set up at commissioning.
After that the Gateway RCD became the problem there was a lot of investigation done including swapping out the gateway but it seemed that the combined earth leakage across my 2 CU RCD's was over 30ma but not sufficient to trip the CU RCD's 30ma each. My installed said things like USB chargers and the like can contribute to the leakage and we have them all over the house. We also have 2 large Solis inverters.
GE then recommended the 100ma RCD in the gateway. So as to match the same manufacturer as the original, my installer had to source this from abroad as they were like rocking horse poo at the time but preferred to do this rather than use one from another manufacturer.
The upshot of all this was that when testing, by dropping the grid from the gateway switch, things worked fine as long as solar was below the levels the gateway could distribute and SOC was below 80%.
However, on very odd occasions we have had the odd blip where either gateway or one of the CU RCD will trip, or the system will so the 20s reset with no trips. This may or may not be related to short blips on the grid but varying degrees of SOC and solar are involved.
In the end we just accept it as its impossible to fault find without debug level monitoring of everything involved in what is a pretty complex scenario. T-M explained the N-PE relay much better than I could have!
I dont believe we have ever had the restart loop you describe but if it is repeatable and you have a split CU you could try taking each side of the CU out the equation to narrow down. Does it actually trip the gateway or CU RCD anytime during the looping?