Jim It's just the mains ac that trips. The PV and battery are still connected to the inverter. To shutdown the inverter, it will need to be isolated from all sources of power; hence the AC supply; PV supply and battery supply isolators to off.
Jim I want to add a CT to the battery
To enable your solar plant to be visible to the Zappi and myenergi app, an additional CT needs to go on the AC connection between the inverter and the consumer unit. I don't believe myenergi offer battery monitoring per se. The benefit of a CT is that it can be clipped onto the outside of a conductor without interfering with any connections.
Jim once the RCBO is off the whole lot is off and safe?
No, that's not a good assumption to make. As mention earlier, the inverter will still be powered by the PV and/or battery and some internals are likely to be at 240Vac. To fit the CT in the GE mini CU, you need to isolate it from all sources of power. This means opening the connection to the main CU (open the MCB there) and opening any connections to/from any inverter - that's the (usually) red isolator next to each inverter. However, unless you're confident about doing this and are able to test the connections inside the CU with a meter, I strongly recommend you ask a sparkie to sort it for you.