Do you have 1 RCD for the entire consumer unit or is the unit split with 1 main CB and a couple of RCDs?
Do you know how old the consumer unit is and I assume you are also charging an EV at the same time as charging the battery? If so I'd expect to see around 11kw peak demand from the grid in those conditions - around 50-60A of current draw.
If it's tripping the RCDs under high load then it's likely to be a short to earth under high load conditions only, unless you have a 10kw plus electric shower it's unlikely you'll have made those sort of demands on the house circuit before.
The installer should have certified the PV, battery circuit and EV charger etc but isn't obligated to check any other aspects of your consumer unit as long as it all looks safe during install.
Can you read the Amp rating on the RCDs? They tend to be around 60A total load rating so depending again on how stuff is wired up in your consumer unit it might be exceeding that value too.
RCD trips can be caused by anything and the recent install might not even be the reason - I had a random RCB trip post PV etc install but it's got its own consumer unit - that said my existing unit was accessed. Cue lots of investigation as it was on the socket ring main (only have 1 for everything but the kitchen) and it eventually turned out to be a 1mm hole in the live insulation just touching the head of the backbox screw. It had been like that for over 2 years as I changed all the faceplates and banged out the single sockets to doubles when we moved in.