Not sure this very latest data-sheet for the 5 kW Gen2 hybrid is accurate. The previous version indicated a maximum total DC input of 6500 W, which is in line with the size of over-provision on many other brands of inverter.
I have an East/West roof approx 30 degree slope, with 6x410W East(-88deg) and 10x410W West(+92deg) installed. By using PVGIS5 to predict maximum insolation, my conclusion was that at 1300 BST the peak power would be with insolation of 800 W/m2 on both sets of panels at that time. There is a higher peak for one side at other times of day, but the drop off at that time on the other side is greater.
Any PV panel data sheet states the output under NMOT conditions which happens to be 800 W/m2, so multiply up that power value by the number of panels.
My panels would give a figure of 312 x 16 = 4992 W.
You really need to have the datasheet for your specific PV panels in order to check the other limitations such as maximum open circuit voltage at low temperatures. This is usually 1.25 x the Voc stated figure x the number of panels in the string.
Having 2 strings in parallel wired to 1 inverter input will likely cause problems, as 2 x say 8 or 9 Amps is 18 Amps which is above the rating of the inverter.