cluelesscris
I think I have now got to the bottom of what is going on with my install and why I am getting grid over voltage errors that knock the inverter into error status, sometimes for hours and hours on end - even when the VAC figure on the portal drops to ‘normal’ levels the inverter frequently remains in error state for much much longer. Sometimes I spot it and restart the inverter from the portal which then gets it going again
e.g.
There are I believe two problems. One is a sporadic supply over voltage, these usually only last 5 minutes or so and can be seen at odd hours of the morning or night. When I have fixed/got a way forward with the big problem (see below) I will probably raise these with the DNO, but for now these are not my real concern.
My big issue is the number and length of what I can only call self-induced over-voltages. These happen a LOT and for a long period of time, and I think are happening more frequently. I’ve had 518 notifications since January on the inverter that has the two batteries connected and most of these are I believe self-induced.
Our system comprises of 28x 380w solar panels (plus a separate 16 panel 4kW Growatt inverter FIT array) and as there are so many panels the installer had to fit two 5kW Hybrid inverters with the panels split across the two inverters. As of two weeks ago I now have two batteries, a 5.2 and a 9.5, both connected to the inverter with 16 panels on it, with no batteries on the other inverter (with 12 panels).
Basically its the second inverter that’s dumping its AC power into the house that is causing the over-voltage and is knocking the first inverter into an error status.
When I turned the second inverter off the first inverter then ran for the remainder of the day and all the next morning there were only 3 over voltage errors, all of which cleared within 5 minutes. But when I turned the second inverter back on I had 11 further errors this afternoon, some of which were 10 or 15 minutes long, and today was a grey overcast rainy day so little solar. Turning the 4kW FIT array off didn’t make any noticeable difference to the over voltage errors so I have been able to leave it on.
I now know that this is called a plant setup and GE don’t recommend it. I spoke to their technical support today and they mentioned the ‘in manufacturing’ box to enable the multiple inverters to talk to one another, but at the moment as the guy explained to me, the two inverters are not communicating to each other in any way which is why GE don’t recommend it. Also of course the AC power generated by the second inverter has no way of being stored in the battery as both batteries are connected to the first inverter. I did ask about moving splitting the batteries across the inverters (and have seen other forum posts where the batteries keep charging and discharging each other) and GE didn’t advise that. Their advice was to leave the second inverter turned off.
I am waiting to receive a call back from my installer to see what they have to say about why they’ve designed and installed a system that GE’s website FAQ’s says they don’t recommend. Turning the second inverter off is not something I really want to do but if it means that at least half of the system works and can charge the batteries from solar then it is something, but means I have a paid for a lot of kit thats going to be turned off until GE produce this plant solution.
☹️