#1 dm0806

Quick question regarding this error, whenever I switch off a fuse on our fuse board (recently the first floor lighting), I get this error, is that normal? The system sorts itself out as soon as the fuse is switched back on.

S
#2 SteveCook

The EM115 if that is what you have needs 3 sets of wire connections
mains L&N to power it

  • & - to the inverter to give the inverter the readings
    black and white to the CT clamp to get readings

https://midsummerwholesale.co.uk/pdfs/giv-ct-manual.pdf

I presume you mean a particular breaker only, in your case 1st floor lighting that must be being used to provide the L&N

#3 judgepd

Mine is the same, the EM115 is getting it's power from the circuit breaker next to it (downstairs lights) so if I turn that off the EM115 also turns off.

D
#4 dm0806

SteveCook Assume this is the case, will check it isn't anything else that causes it, Thanks.

D
#5 dm0806

judgepd Thanks, makes me comfortable everything is as it should be!

#6 judgepd

dm0806 It might not be correct to do it like that...but at least there are 2 of us!

T
#7 TX200

Mine has its own MCB, its own switch and its own box on the wall. Treated like royalty. 🤣