Unless its changed its 100V minimum (but you would need to check the specs on your equipment)
ZmGahH6yQBe
I think its safe to assume that VPV1 is the string with Tigo Optimisers fitted to them as, dependent on which model and how they have been installed in conjunction with your PV Panels, they limit the maximum output to the following;
Maximum power: 500W
Maximum voltage: 90VDC
Maximum current: 12ADC
Maximum string voltage 1000V/1500V
Also if you look at VPV2 you can see that the following calculation - V x A = W
eg. 196 x 2.4 = 470.4 (its within tolerances) 199 x 11.2 = 2228.8
The fact that you have no output on IPV1 or PPV1 would seem to indicate that their is a connection fault on that string.
There is an alternative error that could have occurred and they wired those panels with optimisers in Parallel (rather than in series).

If you wire the panels in Series you ADD the voltages of each panel together but the current stays constant.
Using this panel as an example: 41.2 x 6 = 247.2V x Current (Amps) 11.7 = Power (Watts) 2.892kilowatts
If you wire the panels in Parallel you ADD the Current of each panel together but the voltage remains constant.
Same example 11.7 x 6 = 70.2 Amps x Voltage 41.2 = Power (Watts) 2.892kilowatts
Its seems too much of a coincidence that the VPV1 is so close to the Tigo Optimiser maximum voltage of 90V.
It's either a faulty string, wired incorrectly or they just installed a Single Optimiser at the end of that string (saving them time and money) but "ballsing" up your install.