All of this is based on my setup of 7.2kWp PV, HY5.0 Gen2 and 9.5 battery. Inverter firmware is D0.906-A0.906
I found an interesting, and niche useful thing for maximising PV on oversized arrays, that I haven't seen mentioned before. When the battery mode is set to Timed Export, in the "off time" when the battery normally neither charges or discharges, then it will top slice the PV. So if PV exceeds AC limits, it will dump PV to the battery before throttling.
Also worth mentioning that when you have Timed export or Timed discharge, that during the timed period, it will max out the AC output, but it will take PV first. So if you set the Timed Export/Discharge on period during a sunny day, if the PV is high, the battery discharge is small or 0. In fact in the extreme, the battery will charge from excess PV, during the timed Export/Discharge on period.
Timed export / Timed discharge max out the AC output, not the battery discharge. Maxing out the battery is a secondary effect.
Might be useful to others trying to maximise export and PV production. Downside is that the battery will not provide to the house, or necessarily fully fill during the day. However worth thinking about as part of an automation.
Background:
Several posts talk about how to deal with clipping ( where your PV exceeds your inverters max AC output).
As the Hybrids can DC charge the battery then the actual max is the AC limit + the DC Battery charge before the PV is throttled back.
In my case, on a typical sunny day, Eco prioritises filling the battery over export, the battery is full by lunchtime. Then the system clips until 3-4 pm when the sun is lower. Also the inverter on current firmware doesn't seem to handle clipping well, so it is all over the shop in terms of PV even on a cloudless day with the battery full.
I was experimenting with using Home assistant to vary the charge rate on the battery to attempt to top slice, so effectively prioritise grid export over battery fill, and as a consequence of testing it I was trying all the different modes on a day with high and low PV production through the day.
What the battery modes actually do.
There are a lot of posts on here about the different modes and whether they are broken or what they do. As a newbie I found them often contradictory, so I wanted to test for myself. My opinion is that they do exactly what it says on the tin, its just that the label is badly written :-).
Timed export and discharge have two modes once set. The ON period, between start/stop times, and the OFF period for the rest of the day. So once set, they change the behaviour of the Inverter 24/7, as long as they are set. They don't revert to Eco ( arguably Timed Discharge does).
Both Timed Export and Timed Discharge in the ON period will try to max out the AC limit of the inverter using PV then Battery. The AC power is then used by the house, or sent to the grid. So during the ON period I don't see a difference between Timed export/discharge.
During the OFF period, Timed Discharge acts like Eco. Timed Export neither charges or discharges, apart from in the scenario above of over PV production, or if the battery is below minimum SOC.