Davegreen1
Timed Charge 02.00 - 05.00
Timed Discharge 07.00 - 10.00
Timed Discharge 16.00 - 19.00 (After the battery has topped up from PV)
Why did you want the 7 to 10 discharge ?
On my system at least ( there seems to be some differences between experiences with this. so your milage may vary),
you could do:
Timed Charge 02.00 - 05.00
Timed Discharge 16.00 - 19.00 (After the battery has topped up from PV).
Would give you full battery at 5.00, run on battery till sunrise, then "eco behaviour" till 16:00, then start to attempt to max out the inverter AC from PV and battery till 19:00, or when your battery goes flat.
What I dont like about this for flux set and forget, is that if you cant set a battery minimum soc to preserve some of the battery during the 16-00 - 19:00 window, because it is a single value for both inside and outside that time. So if you did hit that limit, then the battery would retain charge, but not use it at any other time till the soc limit was manually reduced.
You can restrict the window to say 17:30 to 19:00, so that you "usually" have some charge left at 19:00, or try one of the automation options.
A fairly simple automation that only plays with that soc limit could be set up with HA or similar, leaving the inverter itself to do all the rest of the work, but once you need HA for part of the work, it might as well do all of it.