Type AC ---> Type A ---> Type F (used in industrial 99%) ---> Type B
It should be noted that the different types of RCDs (AC, A, F and B) are nested one within the other like Russian dolls: type B, for example, also complies with the requirements of type F, type A and type AC.
So the reason they say you should use a Type B is that it is the only model that is equipped to deal with Constant or Pulsing DC currents, which could conceivably leak into your system and cause nuisance tripping.
In fact we had exactly this issue but then the installer came out and installed a dedicated mini consumer unit for the PV.
It's only fairly recently (last 2-3 years) that Type B RCD's even became available and many manufacturers still don't appear to offer them.
As it's now compliant to only install same brand switchgear into consumer units (ie Hager into Hager) it's pot luck if you can finding a Type B RCD from the manufacturer of your consumer unit.
Hager offer 25A & 40A versions at £300+VAT, Fuzebox have a 63A, thats about £120+VAT, Lewden only introduced them in 2021, doesn't look like BG have one currently nor Live, nor Premspec/Verso, Wylec list price is around £400-£430+VAT
TLDR if it was a legal requirement from either the Electrical Regulations and/or MCS certification then installers would be fitting them (regardless of cost) and simply pass on the added expense to the customer.
If you want something to worry about I would be more concerned with the increasing Neutral faults on the power grid. These will essentially fry every electrical component you have installed.
https://www.northernpowergrid.com/news/grimsby-neutral-fault-customer-update#:~:text=The%20fault%20occurred%20at%2002,to%20internal%20electrics%20and%20appliances.