Small experiment as I knew today was going to be a good PV day. Aim was to see how the inverter coped with various loads etc whilst the inverter combined with PV was capable of supporting all house hold load without having to draw from the grid.
Started at 0900 and according to my smart meter I'd imported 7.47kwh at that point, finished at 1430 at 7.59kwh as my last cup of coffee pulled 100w of grid support (tracking demand on the Myenergi app).
So worst case that's 140wh over that 5 and a half hours due to inverter lag or 3.37p at 24.14p per unit.
Few points to note, I've done 3 loads of washing with demand for heating the water at around 3kw, various cups of coffee, microwave for soup for lunch, 5kwh of grid export, 2.4kwh into the Eddi, 2.2kwh in the Zappi which has had at least 10 interrupt cycles now due to transient loads plus TV on and off, central heating boiler and pump cycles etc.
Given those high transient loads I think 140wh is pretty good, the washing machine has pretty much been on constantly over the period, shame the EV wasn't about when it was sunnier and I didn't export that 5kwh to the grid!
Worth also noting the due to having to cycle the Zappi it went through a charge ramp up check which pulled 800w from the grid briefly. Faff with frequent disconnects causes my car to lock out the charge after 5 reconnects as it sees it as a dodgy charger.