My hybrid inverter has two strings of panels. The top string is 7 panels and the bottom is 9. I have been watching the generation of each string and I am a bit confused with the results. My thinking was that if I took the production for string1 and divided it by 7 I'd get a value per panel and then if I took the generation of string2 and divided that by 9 I would get the per panel value of that and the two values would be roughly the same with no shading. What I in fact see is that the values are not the same, the string2 average per panel is always around 90% of the value of string1. Is my thinking wrong or is this pointing to an issue with one of the 9 panels on string2?
If there is a problem with strings2 then it doesn't look like an entire panel is dead as if I divide the string2 generation by 8 it still doesn't match up.
Examples from the GE cloud console today. The roof is not shaded at either of these times:
16:44 (after an hour of solid sun):
String1 - total 1849w - average 264w (7 panels)
String2 - total 2185w - average 243w (based on 9 panels) - 273w (based on 8 panels)
Peak at 15:08:
String1 - total 2227w - average 318w (7 panels)
String2 - total 2629w - average 292w (based on 9 panels) - 328w (based on 8 panels)
The comparison has been about the same since the panels were installed last year and I wanted to get some other opinions before I go back to the installer and ask for some advice.