Yesterday Eon came and fitted a new economy 7 (multi-rate) smart meter. Very long story as to why I’ve had 4 different meters over the last year, but at its core Eon can’t upgrade an existing smart meter configuration from single rate to multi-rate.
In the process the engineer tidied up all the wiring in my meter box which was a rats nest of cabling after the heat pump and then solar battery systems were fitted.
In doing all this work he had to disconnect the CT clamps (I have twin AC5 hybrid inverters) and then reconnect them afterwards. He took a picture of them beforehand and used that when he clipped them back on.
After the power was restored we noticed on the GE app that the house was pulling 6-8kW which the panels alone were not able to provide so the batteries drained down through the afternoon to supplement the demand. I thought it odd that it was a sunny day and the batteries were not charging but put it down to things like the heat pump and hot tub restarting themselves. I did check the CT clamps and they appeared to be the right way round.
This morning, same thing. Batteries fully discharged, house demand was running at 8-12kW all the time, panels not generating enough to support the load so pulling in 7kW from the grid and this load started at about 6am this morning.
Very confused as to what is drawing 12kW all the time. Went round turning off circuits to see where the demand was coming from and couldn’t isolate it and stop the current draw.
Re-read the installation manual for the CT clamp direction, and just to see if it made a difference, swapped the CT clamps round. Amazing, the house load dropped to just 2kW and the batteries started charging up.
My summary is that the Eon engineer installled the CT clamps the wrong way round, and because I also have an existing 4kW FIT array (with an existing Growat inverter that isn’t monitored by the GE system), when the FIT array is generating power that the house isn’t using, the CT clamps were recording the FIT export as an import and were draining the batteries to supply this phantom house load.
Swapping the CT clamps round solved the problem.
In diagnosing and fixing the problem I think the GE installation manuals are still not clear about the installation of the CT clamp.
The “installer training manual V12” shows the CT1 arrow pointing towards the grid, the L on the grid side and the K on the load side. But the text says that the arrow should point towards the load.

A previous installation manual “Installation Manual Givenergy All 2021” shows the L on the consumer unit side, K on the grid side and that the arrow should point towards the consumer unit.

My system is now setup with the second of these, the L on the consumer unit side and the arrow pointing towards the consumer unit and its working fine.