3.6KW Gen 2, 911 firmware, 11 x Trina 425W on one string. It's been working fine for weeks, but today is the first proper sunny day with this firmware.
At around 1645 today it stopped PV generation, stopped discharging the 100% full battery to fulfil house load, and also appeared to stop reading house load and grid import from the EM115. Full sun and about 3.6KW potential generation.
It was still uploading data to portal, and responded to a "Restart Inverter" from portal which brought it back to life fully @1715

My best guess looking at the inverter data logs is that once the battery is full and the PV power is over 3.6KW is starts to derate the output to restrict power. This in turn increases the string voltage over 500V, at which point it briefly switches off the PV. After a couple of these 'incidents' it seemed to switch off PV and battery discharge permanently.
The V2 inverter spec has MPPT range up to 550V, so I've no idea why 500V seems to be the trigger point. Can @TheDragon (GivEnergy) or someone else advise, or take a look, please?