I've tried to stay a little out of this as I'm aware I come across as captain criticise GE quite a lot but I guess there's not many takers on this one.
I think for some context some images of what the gateway actually looks like with lids on & lids off are needed:

So you first need to open the front door using the key, you are then presented with the breakers and their covers, once those are removed (thumb screw locks these in) then you do get to the insides with exposed parts. But to get that far you have gone through several steps & warnings.
I presume his concerns relate around the incoming unshrouded bars on the right which yes would technically be live even with all the MCB's switched off. I'm half and half on this, personally I'd prefer those to be shrouded, these are new and somewhat confusing layout. Your electrician is likely talking about the regs around basic protection & also enclosure of live conductive parts?
Basically following ALARP would I expect someone who has never worked on these (or worse an enthusiastic DIY owner) to be able to put their hands on something still live in there beyond the incoming tails - probably not - is it reasonable that a form of isolation/insulation could be provided -yes - therefore it would be safer for them to be shrouded (the ones on the left hand side are so this does seem an oversight - room for improvement on V2?)
Beyond BS7671, I guess you could ultimately work this back to Electricity at work act:
Regulation 14
“No person shall be engaged in any work activity on or near
any live conductor (other than one suitably covered with
insulating material so as to prevent danger) that danger may
arise unless:-
(a) it is unreasonable in all the circumstances for it to be
dead; and
(b) it is reasonable in all the circumstances for him to be at
work on or near it while it is live; and
(c) suitable precautions (including where necessary the
provision of suitable protective equipment) are taken to
prevent injury”
I do however have a little more concern as to the EM meters being fed straight from the busbars (so basically protected by a 100A MCB) which did seem an odd choice (told it's fine from GE's stance.)
Also had some comments about the Type AC RCD's being used for the AIO & PV inverter, mitigated by the fact that the Givenergy AIO has it's own built in protection (IEC62109-2) however it's up to the installer to check that whatever PV inverter they use is equally the same standard lest it blind the breaker.