geoffreycoan As an update to this thread I applied for G99 proposing the installation of a 3.6kW hybrid inverter and 3.24kW of panels, and a 5.2kWh battery. Response from the DNO was quick and helpful and they approved the installation with an export limit of 7.48kWh.
So I now have 1) a FIT installation with 3.6kW of panels, 2) An AC coupled inverter with 9.5kWh battery, and 3) a 3.6kW Generation 3 hybrid inverter coupled to 3.2kW of panels with an additional 5.2kWh Gen 1 battery. (3) is nearly installed but as yet uncommissioned. The FIT export has been changed to SEG export(currently with GoodEnergy who initiated the change due to the presence of a smart meter). Following commissioning and notification of MCS certification the DNO will grant me an export MPAN number.
I am less concerned with export than with the efficient use of the system in meeting the house demand and charging a hybrid vehicle without consuming grid energy. At the moment using the installed FIT solar and the AC inverter the system works pretty well coupled with a Zappi charger. An export limit is set on the Zappi which means that the AC inverter won't discharge to the vehicle, leaving the battery empty and unable to contribute to the house load in the evening.
I have two EM115 meters running into the AC inverter which tell the inverter when there is grid import, and also what the solar output is. I also have three myEnergi CTs linked to the Zappi via Harvi wireless links; one which monitors grid import/export, one which gives the solar output, and one which monitors the AC inverter. An additional complication is that the Zappi, AC inverter and now the hybrid are wired to the garage consumer unit which is fed from a 63A MCB in one of the house consumer units.
I have a couple of questions re the additional CT/meters I may need to install and where.
1) Presumably the RS485 bus carrying the modbus info from the EM115 meters can just be connected from the AC inverter to the hybrid, giving the hybrid the same info as the AC inverter(grid import/export and FIT solar output)? Or will I need separate meters - I cannot see why that might be the case since the info would be identical?
2)I would also install an additional CT for the hybrid output to the Zappi to show the solar output and enable charging when available?
3) I would install an additional CT on the hybrid output for the AC inverter? Can this be done in addition to using the EM115 meter information?
So with a combination of monitoring solar output and grid import/export by the Zappi charger, and timed charge/discharge settings in the inverters, I should be able to charge the car when there is an excess of solar, but preserve some or most of the battery charge for the evening house load. I would also be able to top up the batteries using the cheap overnight tariff on Octopus Go at night. An additional advantage of the two battery connected inverters is the ability to deliver higher power levels to the house in the evening.
It is somewhat complicated but basically using the Zappi to limit charging when there is the possibility of battery drain is the aim, whilst having both inverter/battery sets to reserve energy for evening house loads.
Am I on the right track here? Any comments or help greatly appreciated as ever.