Disruption after fitting a smart meter

10 comments started 2023-12-05 last 2023-12-06
CommisioningGivEnergy ProductsBattery
J
#1 Jacqui

We had a smart meter fitted today, and now the inverter has entered a cycle of charging the battery from the grid to 100%, then discharging all of that energy back to the grid. It is dark, so there is no solar input. How do I reset the inverter to stop this happening?

R
#2 rjp

Sounds like the installer has moved or reversed the CT clamp that the inverter uses to measure current?

J
#3 Jacqui

Thanks for this, but I am not sure what to do about it. Can it be reversed back again?

J
#4 Jellybaby

Jacqui You should be able depending on the CT clamp open it up, flip it over then clip it back on, if you are not comfortable with this then they would have to come out pronto to sort it.

J
#5 Jacqui

Jellybaby Thanks - looks like I need to get someone out to fix it pretty quickly.

J
#6 Jellybaby

Jacqui It should be a super quick fix so they should be able to get someone out same day, if not tell them you will file a complaint as they have rendered your equipment useless and cba to sort it pronto

S
#7 SteveCook

Do search for EM115

V
#8 Vestas

It'd probably be helpful just to shut the inverter down if Jacqui isn't happy about turning the current clamp around then turn it on after its been sorted 🙂

Installers should have left docs telling you how to do this....

J
#10 Jacqui