Firmware D0.913-A0.913

12 comments started 2023-12-24 last 2024-01-10
GivEnergy ProductsHybrid
S
#1 Stephen

Has anyone upgraded to D0.913-A0.913 firmware on a Gen 2 5KwH Hybrid inverter? If so are you having battery discharge issues or is your system still running as designed?

#2 Lofthouse

Stephen I upgraded to 913 a few days ago, without any apparent issues. The only odd thing I found was that after the firmware upgrade completed, a command was sent to the inverter to set Enable EPS to True. As I don’t have an EPS setup, I set this back to False using the Remote Control section of the GivEnergy Cloud Portal.

What battery discharge issues are you seeing ?

S
#3 Stephen

Lofthouse thanks gor replying. My other post yesterday about inverter stuck charging at 290W has more detail. Text copied below, but more detail with screen shots in other thread.

Since I upgraded the inverter firmware yesterday evening my battery has been stuck charging at around 290W. Tried hard and soft resets of the inverter. Quick settings for pause and discharge do not work, but charge does. Reset everything to defaults and checked each setting in the portal. Nothing has rectified the issue yet, anyone any other ideas?

I have a 5kw Gen 2 inverter on firmware D0.913-A0913 and a 9.5 KWh battery.

#4 Lofthouse

So after the resets, have you been able to check the settings in the Remote Control section of the GivEnergy Cloud portal ?

I would be looking particularly at the settings:

AC Charge Upper % Limit - should be 100
Battery Reserve % Limit - should be 4
Battery Charge Power - should be 3600
Battery Cutoff % Limit - should be 4
Inverter Max Output Active Power % - should be 100
Enable EPS - should be Off (unless you have EPS wiring)
Battery Charge Power Percentage - should be 100
Pause Battery - should be Not Paused
AC Charge 1 Start Time - recommend 00:00 for now
AC Charge 1 End Time - recommend 23:59 for now

For each setting, press the swirly arrow to re-read the setting from the inverter - do not trust what is initially displayed on the screen …

If you get the odd Inverter Timeout message when re-reading a value, don’t worry, I get that too …

I really feel for you, especially at this time of year ☹️

S
#5 Stephen

Lofthouse Thanks for copying all the settings. I have checked all of these and they are all correct. I have also changed them to try to kick it back in to action I will check again though just to make sure. Thanks again.

R
#6 rio911

I have the same HY5 Gen2 inverter. Today, I got the message for a new firmware, I'm assuming it is 913, as I'm on 912 atm.

What is the general consensus? Upgrade or wait? I don't have any major issues with the current firmware. The only thing is that timed discharge/export will do 4kW from the battery?!?!?!

#7 Lofthouse

For me, in these days of Savings Sessions, the additional discharge was very handy, so I pressed the button and it all worked as expected, but I did that before the festive season kicked in.

For @Stephen, he is now stuck with a misbehaving battery on Christmas Eve.

So applying due weighting to each outcome on our sample size of two (!), I would definitely advise you to wait until the GivEnergy Support desk is open again …

S
#8 Stephen

Lofthouse Thanks to Jacob Smith from GivEnergy, who remotely accessed my inverter at 23:45 on Christmas Eve, my system appears to be back up and running. Excellent service.

#9 Lofthouse

Stephen Wow, that is above and beyond!

S
#10 Stephen

Stephen My inverter has worked fine all night, discharging to supply the house and a timed charge at low rate and then resumed discharge post that. The issue was not to do with any settings we have access to. It took a couple of remote reboots by GivEnergy of the software to kick the discharge back in to life. Thanks to those who posted helpful comments yesterday.

Merry Christmas

V
#11 Versatile

Stephen Hi Stephen,
We are experiencing the same issue. I was wondering if your system is still up and running?
Cheers

P
#12 paulwindy

Lofthouse with 913 do you get more charging slots like the gen 3 now ? I have the Gen 2 on 912 with only 1 slot