Adding new 9kwh battery

6 comments started 2022-04-07 last 2022-04-08
GivEnergy ProductsAC CoupledHybridBattery
J
#1 jd

Givenergy say that batteries connected in series should always have the largest capacity as the master. As the 8kwh is now discontinued according to suppliers across the country, does that mean adding a new 9kwh means a messy rewire to try to swap the order of batteries?

Z
#2 Zakalwe

Its controlled by dip switch settings in the battery, AFAIK

J
#3 jd

That's correct thanks, but in the training givenergy said that the largest battery should be master followed by smaller batteries as slaves. As the 9kwh is larger than any existing batteries and the 8kwh is end of life, do we have to swap things about if we're expanding the overall capacity of the system?

T
#4 Tim

jd No, I think @Zakalwe has the answer. The existing wiring could remain; the new battery daisy-chained to the existing battery by the DC connections and the Modbus cabling also extended. The existing battery would have it's DIP switch tweaked to make it a slave device and the new higher capacity battery would be the master (DIP switches all set to zero).

Z
#5 Zakalwe

jd

Yes, but it doesn't say anything about the wiring of the batteries. I imagine it's like in the days of IDE hard disk drives...youbhad to have one master on the IDE bus and then up to 3 slaves. Changing jumper positions on each individual drive designated which was master and slaves.

J
#6 jd

Zakalwe Cool thanks. I would normally ask support, but they just don't reply, I think they are inundated with the influx of new installs. It's a shame they don't add to the FAQ as they answer important questions