I am currently in the process of getting quotes to install a solar PV system, with a battery. The installer has quoted for a Giv-HY 5.0 'G2' (so I assume 2nd gen variant) inverter.
Looking at the datasheet for the inverter and the paired battery, it looks like the maximum power available from the battery alone (so later in the day, when no solar generation), would be just 3.6kW. So if my house load is 4.4kW (two ovens in use), I would presumably still be importing 0.8kW from the grid.
Have I understood the datasheet correctly, or can the inverter actually supply the full 5.0kW from the battery alone?
2nd Question
I'm also considering if I could run two batteries and two inverters in a parallel, so that if one should fail, I would still have 50% of the system in operation (assuming the faulty side was isolated). I will have two solar strings, so each could be connected to its own inverter/battery pair. Can this be done, or are there good reasons not to go down this route (apart from the higher price)?
Thanks
Chris