I have just had an installation completed. I have 33xJinko 440W panels (14.52kW (about 10kW facing West / 4.5kW South) feeding via 3 strings into a Fox ESS 10kW AC inverter into the AIO gateway. Today (The sunniest day yet), the 32A breaker in the gateway tripped, leaving the Fox ESS with a Grid Lost Fault.
My question is: seeing as my generation is peaking around 10.3kW, and today, for the first time, this? Could this have caused its 32A breaker to trip, or did its 32A breaker cause it to trip? It needs to be updated to a 45A.
Is that inverter inadequate to handle the system? I presume I am wasting those additional panels on the roof in the height of summer only as an additional export, but they will pay me in the winter, as I'm not overpowering the inverter, such as a 15kW during sub-optimal production.