With a basic installation, only 1 x EM115 import/export meter is installed with a CT on the grid cable (usually close to the main utility billing meter). This meter connects to the inverter via a Modbus comms cable, and is able to provide live values for power, voltage, current etc along with cumulative kWh energy values.
Given the cloud portal provides energy values for the ac grid import/export, ac inverter import/export, dc PV generation and dc battery import/export, presumably there are other metering devices built-in to the inverter to provide these values.
So the question is, how accurate are the inverter built-in meters, and is there any benefit in adding a 2nd EM115 to monitor the ac inverter import/output and connecting it on the same modbus daisy-chain network? It is shown as an option on one of the install guide schematics, along with an option with 2 x EM418 meters for FIT installations.
My thoughts are that the 2nd EM115 could provide the following benefits:-
1/ It would at least keep recording the cumulative energy readings during periods when the inverter has lost the WiFi/internet connection back to the cloud servers.
2/ Keeps the cumulative import/export values in the event of an inverter failure/reset, that can be read from the EM115 meter display.
3/ Possibly more accurate than the metering built-in to the inverter.
Any thoughts or experiences on this?